01 Jun 2020 23:59 #8261
by karthik61
Replied by karthik61 on topic DC module deviation from STC
Good Day Paul,
Decreasing GCR reduced the module loss. But I would like to keep a row spacing of 1.75 m between two arrays.
Attached the PV system design for reference.
And I kept the same pitch: 1.75 m and GCR: 95.4% in PVsyst and I got less module loss and more Annual energy output under same conditions.
Thanks,
Karthik.
Decreasing GCR reduced the module loss. But I would like to keep a row spacing of 1.75 m between two arrays.
Attached the PV system design for reference.
And I kept the same pitch: 1.75 m and GCR: 95.4% in PVsyst and I got less module loss and more Annual energy output under same conditions.
Thanks,
Karthik.
Attachments:
Please Log in or Create an account to join the conversation.
- kon
Less
More
- Posts: 2
02 Jun 2020 01:45 #8262
by kon
Replied by kon on topic DC module deviation from STC
Hi all,
How exactly the "DC module deviation from STC" is calculated? I cannot find a good reference and in some of my calculations this parameter enhances the performance of the pv-system and I don't understand why.
Best regards,
Konrad
How exactly the "DC module deviation from STC" is calculated? I cannot find a good reference and in some of my calculations this parameter enhances the performance of the pv-system and I don't understand why.
Best regards,
Konrad
Please Log in or Create an account to join the conversation.
- pgilman
Less
More
- Posts: 5423
02 Jun 2020 15:46 #8264
by pgilman
Replied by pgilman on topic DC module deviation from STC
Hi Konrad,
There is a long discussion about the module loss value in this issue on GitHub (see also the link to Issue #197 mentioned in the comments):
github.com/NREL/ssc/issues/205
Best regards,
Paul.
There is a long discussion about the module loss value in this issue on GitHub (see also the link to Issue #197 mentioned in the comments):
github.com/NREL/ssc/issues/205
Best regards,
Paul.
Please Log in or Create an account to join the conversation.
- pgilman
Less
More
- Posts: 5423
02 Jun 2020 16:37 #8265
by pgilman
Replied by pgilman on topic DC module deviation from STC
Hi Karthik,
Based on the information you provided, I calculate GCR = 0.51:
GCR = 1.74 / ( 1.74 * cos( 20 ) + 1.75 ) = 0.514
I used SAM's parametric simulations in the attached .sam file to generate this table showing the annual output and "module deviation from STC" loss for a range of GCR values:
Best regards,
Paul.
Based on the information you provided, I calculate GCR = 0.51:
GCR = 1.74 / ( 1.74 * cos( 20 ) + 1.75 ) = 0.514
I used SAM's parametric simulations in the attached .sam file to generate this table showing the annual output and "module deviation from STC" loss for a range of GCR values:
Best regards,
Paul.
Attachments:
Please Log in or Create an account to join the conversation.
- karthik61
- Topic Author
Less
More
- Posts: 6
02 Jun 2020 23:49 #8267
by karthik61
Replied by karthik61 on topic DC module deviation from STC
Hallo Paul,
Thanks a lot for the simulation.
But in SAM row spacing of 1.75 m is different from the one you calculated (1.74 * cos( 20 ) + 1.75 ).
And also in the attached PV system design, the arrays are closer with a total pitch(row spacing) of 1.75 m only, this leads to GCR 0.954 (same in case of PVSyst)
Thanks,
Karthik.
Thanks a lot for the simulation.
But in SAM row spacing of 1.75 m is different from the one you calculated (1.74 * cos( 20 ) + 1.75 ).
And also in the attached PV system design, the arrays are closer with a total pitch(row spacing) of 1.75 m only, this leads to GCR 0.954 (same in case of PVSyst)
Thanks,
Karthik.
Attachments:
Please Log in or Create an account to join the conversation.
- kon
Less
More
- Posts: 2
03 Jun 2020 01:15 #8269
by kon
Replied by kon on topic DC module deviation from STC
Thank you Paul, very interesting discussion indeed!