System draws from grid, even when enough power could be supplied

  • tmartin
  • Topic Author
More
03 Nov 2016 05:50 #4883 by tmartin
Hi,

When I run the battery module the results show that there is power draw from the grid even when there is enough power from pv+battery to supply the load without the grid. This happens both when I use the SSC battery module and my own matlab code, or through SAM. The draw is not much, typically watts or tens of watts, but it is significant for my use (modeling an off-grid system). Initially I thought that the pv+batt system was undersized, but it seems to be an issue even when I significantly increase the capacity of both.

I've attached a SAM file and a sample image of its output data for reference. This isn't the same model I've been using but it's demonstrative of the problem I've been having.

Is there a way I can avoid drawing from the grid like this?

Thanks,

Tane

Please Log in or Create an account to join the conversation.

  • tmartin
  • Topic Author
More
07 Nov 2016 18:48 #4884 by tmartin
Hi,

Has anyone had a chance to take a look at this? I've continued altering inputs but that hasn't made any real difference.

Thanks,

Tane

Please Log in or Create an account to join the conversation.

  • ndiorio
07 Nov 2016 21:14 #4885 by ndiorio
Hi Tane,

Sorry for the delayed response. To explain what is happening, I'll briefly detail some of the processes going on when energy is requested from the battery.

- If the battery is allowed to discharge during the time period in question, an energy balance is performed, considering the PV energy, and electric load. The battery power required to discharge is computed as [P_battery = P_load - P_pv]. So if for instance, the PV array is producing 20 kW, and you have an electric load of 25 kW, the battery should discharge 5 kW.

- But, the way the capacity and voltage model are setup, the battery voltage changes as energy is discharged from the battery, such that at a constant current level, the power from the battery is slightly less or more than requested. Essentially, a constant current discharge occurs over the hour, starting at V1 (voltage 1) and ending at V2( voltage 2). The total power discharged is thus: P = 0.5I*(V1 + V2), which is different from the power requested.

- Grid power is assumed to fill any deficit from the battery, such that in our example about, if the battery was requested to discharge 5 kW, but only discharge 4.99 kW, the grid is assumed to need to discharge 0.01 kW.
This results in the spike you see.

I agree that this is not necessarily desirable behavior. I will work on adding in additional feedback mechanisms that tailor the battery discharge to be exactly the requested amount so these kinds of spikes do not occur. In the meantime, you could simply remove them, provided they are small. If you're modeling an offgrid system, you could set the utility rates equal to 0, such that it doesn't matter if power is purchased from the grid, thus removing any economic anomalies associated with this behavior.

Thanks,
Nick

Please Log in or Create an account to join the conversation.

  • tmartin
  • Topic Author
More
08 Nov 2016 05:59 #4886 by tmartin
No problem,

Just wanted to make sure my post didn't get lost in the cracks. Thanks for the response and the help; I should be able work out a way to work around this now that I know the reasoning behind it.

It would be great if future versions didn't have this though. Regardless, these modules have been super helpful - really appreciate all your guys' work/help.

Thanks,

Tane