Clipping in the Red
- inreco
- Topic Author
Less
More
21 Dec 2025 09:27 #14426
by inreco
Clipping in the Red was created by inreco
When I run System Sizing with a 710w module and then run again with a 730w module, same database Inverter the MPPT clipping goes into the RED with the 710w module.
I thought that if the modules output (730w) is more than the Inverters rated input only then the clipping would go to the RED. But in this case the lower wattage (710w) module cases the high clipping and changing the quantities of the Inverters up/down doesn't eliminate the high clipping.
What am I not understanding here??
I thought that if the modules output (730w) is more than the Inverters rated input only then the clipping would go to the RED. But in this case the lower wattage (710w) module cases the high clipping and changing the quantities of the Inverters up/down doesn't eliminate the high clipping.
What am I not understanding here??
Please Log in or Create an account to join the conversation.
- Paul Gilman
Less
More
- Posts: 5696
05 Jan 2026 10:18 #14435
by Paul Gilman
Replied by Paul Gilman on topic Clipping in the Red
Hello,
The PV System Sizing macro shows estimated power losses for inverter power limiting and MPPT voltage clipping.
Power limiting is determined by the array power output and the inverter's AC capacity: The inverter limits its AC power output to the nameplate capacity.
Voltage clipping is determined by the array operating DC voltage and the minimum and maximum MPPT voltage rating: The array DC operating voltage is clipped to the maximum (or minimum) MPPT voltage.
The results you describe suggest that the 710 Watt module operates at a higher DC voltage, or that the number of modules per string for the 710 Watt module is higher than for the 730 Watt module.
Best regards,
Paul.
The PV System Sizing macro shows estimated power losses for inverter power limiting and MPPT voltage clipping.
Power limiting is determined by the array power output and the inverter's AC capacity: The inverter limits its AC power output to the nameplate capacity.
Voltage clipping is determined by the array operating DC voltage and the minimum and maximum MPPT voltage rating: The array DC operating voltage is clipped to the maximum (or minimum) MPPT voltage.
The results you describe suggest that the 710 Watt module operates at a higher DC voltage, or that the number of modules per string for the 710 Watt module is higher than for the 730 Watt module.
Best regards,
Paul.
Please Log in or Create an account to join the conversation.
- inreco
- Topic Author
Less
More
- Posts: 62
05 Jan 2026 12:59 #14442
by inreco
Replied by inreco on topic Clipping in the Red
Thanks!