I designed a PV power Plant where where ac nameplate capacity 448 MW but i am only getting 340 MW max. is it normal?
Please Log in or Create an account to join the conversation.
- Paul Gilman
Less
More
- Posts: 5696
05 Jan 2026 10:47 #14439
by Paul Gilman
Replied by Paul Gilman on topic PV Generation Discrepency
Hi Miskat,
A well-designed PV system should operate at close to its nameplate capacity at least some hours of the year.
There are several things that could cause the maximum output to be less than the nameplate capacity. Here are a couple of examples:
Paul.
A well-designed PV system should operate at close to its nameplate capacity at least some hours of the year.
There are several things that could cause the maximum output to be less than the nameplate capacity. Here are a couple of examples:
- Comparing AC output to DC nameplate capacity. Be sure you are either comparing array DC output to the array DC capacity, or inverter AC output to the inverter AC capacity.
- Array azimuth or tilt angle is not optimal.
- Excessive losses: You can use the diagram on the Losses tab of the Results page to quickly find potential design problems such as undersized inverter, to many modules per string causing MPPT voltage clipping, soiling or shading losses, etc.
Paul.