- Posts: 5640
Issue with BESS not charging from curtailed power under interconnection limit in
- Paul Gilman
Less
More
12 Sep 2025 15:17 #14283
by Paul Gilman
Replied by Paul Gilman on topic Issue with BESS not charging from curtailed power under interconnection limit in
Hi Ms. Loan,
I think there is a problem with the logic that controls when the check boxes are enabled and disabled. To enable Battery can garge from grid-limited power, the following must be true:
Paul.
I think there is a problem with the logic that controls when the check boxes are enabled and disabled. To enable Battery can garge from grid-limited power, the following must be true:
- On the Battery Dispatch page for BTM batteries, either Manual dispatch or Retail rate dispatch is checked; for FOM batteries, either Automated dispatch or Manual dispatch is checked.
- On the Battery Dispatch page, Battery can charge from system is not checked.
- On the Grid Limits page, Enable interconnection limit is checked or at least one value in the curtailment array is less than 1e+38.
- Temporarily change the dispatch option to Peak shaving for BTM batteries or Automated dispatch for FOM batteries.
- Clear Battery can charge from system.
- Change the dispatch option back to Manual dispatch.
Paul.
Please Log in or Create an account to join the conversation.
- Đỗ Thị Loan
Less
More
- Posts: 2
13 Sep 2025 08:32 #14287
by Đỗ Thị Loan
Replied by Đỗ Thị Loan on topic Issue with BESS not charging from curtailed power under interconnection limit in
Hi Pauls,
Many thanks for your clear explanation. It really helped me understand the dispatch settings in SAM better.
Many thanks for your clear explanation. It really helped me understand the dispatch settings in SAM better.