12 Sep 2025 15:17 #14283 by Paul Gilman
Hi Ms. Loan,

I think there is a problem with the logic that controls when the check boxes are enabled and disabled. To enable Battery can garge from grid-limited power, the following must be true:
  • On the Battery Dispatch page for BTM batteries, either Manual dispatch or Retail rate dispatch is checked; for FOM batteries, either Automated dispatch or Manual dispatch is checked.
  • On the Battery Dispatch page, Battery can charge from system is not checked.
  • On the Grid Limits page, Enable interconnection limit is checked or at least one value in the curtailment array is less than 1e+38.
The problem is that Battery can charge from system is disabled for manual dispatch so you can't clear the check box. In order to clear the check box:
  1. Temporarily change the dispatch option to Peak shaving for BTM batteries or Automated dispatch for FOM batteries.
  2. Clear Battery can charge from system.
  3. Change the dispatch option back to Manual dispatch.
Best regards,
Paul.
 

Please Log in or Create an account to join the conversation.

  • Đỗ Thị Loan
More
13 Sep 2025 08:32 #14287 by Đỗ Thị Loan
Hi Pauls,
Many thanks for your clear explanation. It really helped me understand the dispatch settings in SAM better.

Please Log in or Create an account to join the conversation.