Grid Limit for Stand-Alone BESS
- Vítor
- Topic Author
Less
More
12 Feb 2025 11:27 #13863
by Vítor
Grid Limit for Stand-Alone BESS was created by Vítor
I am trying to simulate a stand-alone BESS to extract the state of charge curves of the batteries and the power injected into the system. I am considering a grid limitation of 30 MW, however, this limit is only being respected during discharge. During battery charging, the system exceeds -35 MW. Is there any parameter I might be missing?
Moreover, there is a distortion in the power curve during charging. How can I fix this?
Moreover, there is a distortion in the power curve during charging. How can I fix this?
Attachments:
Please Log in or Create an account to join the conversation.
- Paul Gilman
Less
More
- Posts: 5490
12 Feb 2025 11:50 #13864
by Paul Gilman
Replied by Paul Gilman on topic Grid Limit for Stand-Alone BESS
Hi Vitor,
The grid limits only constrain exports to the grid. They do not limit imports. This is explained in the Grid Limits Help topic:
Based on the manual dispatch parameters on the Battery Dispatch page, the battery is only allowed to discharge to the grid during Period 2 from 5pm to 8pm, and to charge from the grid from 10am to 1pm. The time series plot in the screenshot you shared looks consistent with this dispach schedule.
Best regards,
Paul.
The grid limits only constrain exports to the grid. They do not limit imports. This is explained in the Grid Limits Help topic:
Based on the manual dispatch parameters on the Battery Dispatch page, the battery is only allowed to discharge to the grid during Period 2 from 5pm to 8pm, and to charge from the grid from 10am to 1pm. The time series plot in the screenshot you shared looks consistent with this dispach schedule.
Best regards,
Paul.
Please Log in or Create an account to join the conversation.
- Vítor
- Topic Author
Less
More
- Posts: 3
12 Feb 2025 12:13 #13865
by Vítor
Replied by Vítor on topic Grid Limit for Stand-Alone BESS
Hi Paul,
Thanks for the reply!
Is there any chance that the software will implement this feature of limiting energy import in the future? I believe it is very useful because the BESS can use the same power limit authorization for both energy import and export.
The distortion i meant was the spike when the battery starts recharging from the grid (as shown in the attached screenshot).
Thanks for the reply!
Is there any chance that the software will implement this feature of limiting energy import in the future? I believe it is very useful because the BESS can use the same power limit authorization for both energy import and export.
The distortion i meant was the spike when the battery starts recharging from the grid (as shown in the attached screenshot).
Attachments:
Please Log in or Create an account to join the conversation.
- Paul Gilman
Less
More
- Posts: 5490
12 Feb 2025 17:31 #13866
by Paul Gilman
Replied by Paul Gilman on topic Grid Limit for Stand-Alone BESS
Hi Vitor,
I think that spike is a plotting artifact rather than real data. If you zoom in to the graph, you should see it disappear. You can also confirm that by looking at the data itself on the Data Tables tab (or by right-clicking the graph and exporting the data from there).
Adding a limit for grid imports is on our wishlist: github.com/NREL/SAM/issues/1957
Best regards,
Paul.
I think that spike is a plotting artifact rather than real data. If you zoom in to the graph, you should see it disappear. You can also confirm that by looking at the data itself on the Data Tables tab (or by right-clicking the graph and exporting the data from there).
Adding a limit for grid imports is on our wishlist: github.com/NREL/SAM/issues/1957
Best regards,
Paul.