Inquiry regarding pump behavior with full TES in CSP plant simulation
- Pablo Tagle
- Topic Author
        Less
        More
        
            
    
        
            
        
                17 Nov 2023 02:42         -  17 Nov 2023 16:02        #12658
        by Pablo Tagle
    
    
 	
					
                    	
            			
							    
    
            
            
            
            
                                
    
                                                
    
        Inquiry regarding pump behavior with full TES in CSP plant simulation was created by Pablo Tagle            
    
        During my simulations using SAM 2022.11.21 for a CSP plant with a solar tower and molten salt TES, I observed an unexpected behavior. Despite programming the control system for a maximum load equal to the nominal value (for the power block), I noticed that when the hot tank reaches full capacity, the pumps exhibit a slightly higher flow rate than the nominal setpoint (See attached figure. Mass flow TES cold out in blue, Mass flow TES hot out in orange, and TES charge state in brown). I am curious to understand the reasons behind this phenomenon. Are there specific considerations, whether related to performance, costs, or other factors, that could explain or justify this behavior?
 
    
    
        Last edit: 17 Nov 2023 16:02  by Paul Gilman.        Reason: Insert image as attachment    
            Please Log in or Create an account to join the conversation.
- Paul Gilman
        Less
        More
        
            
    
        - Posts: 5665
            
        
                20 Nov 2023 09:08                #12663
        by Paul Gilman
    
    
            
            
            
            
            
                                
    
                                                
    
        Replied by Paul Gilman on topic Inquiry regarding pump behavior with full TES in CSP plant simulation            
    
        Hi Pablo,
Could you attach a .sam file that demonstrates these results, if possible also with the weather file (.csv) that you are using?
Best regards,
Paul.
    Could you attach a .sam file that demonstrates these results, if possible also with the weather file (.csv) that you are using?
Best regards,
Paul.
Please Log in or Create an account to join the conversation.
- Pablo Tagle
- Topic Author
        Less
        More
        
            
    
        - Posts: 2
            
        
                29 Nov 2023 04:35         -  30 Nov 2023 15:36        #12702
        by Pablo Tagle
    
    
    
            
            
            
            
                                
    
                                                
    
        Replied by Pablo Tagle on topic Inquiry regarding pump behavior with full TES in CSP plant simulation            
    
        Dear Paul
Thank you for your prompt response.
Unfortunately, I am unable to share the simulation files due to constraints related to a non-disclosure and confidentiality agreements associated with the project.
However, upon further investigation, I discovered that the parameter "maximum turbine over design operation" in "Power cycle" tab was configured with its default value of 1.05. Subsequent to modifying this parameter to 1, the observed issue was resolved. It is noteworthy to mention that I am uncertain if this parameter is directly linked to the control strategy, but its adjustment appeared to have a significant impact on the observed behavior.
I hope this information proves helpful in further questions.
Best regards.
     
    Thank you for your prompt response.
Unfortunately, I am unable to share the simulation files due to constraints related to a non-disclosure and confidentiality agreements associated with the project.
However, upon further investigation, I discovered that the parameter "maximum turbine over design operation" in "Power cycle" tab was configured with its default value of 1.05. Subsequent to modifying this parameter to 1, the observed issue was resolved. It is noteworthy to mention that I am uncertain if this parameter is directly linked to the control strategy, but its adjustment appeared to have a significant impact on the observed behavior.
I hope this information proves helpful in further questions.
Best regards.
        Last edit: 30 Nov 2023 15:36  by Paul Gilman.            