Issue with the DOD Results

  • Antonio_Garcia
  • Topic Author
More
15 Sep 2023 08:22 #12502 by Antonio_Garcia
Issue with the DOD Results was created by Antonio_Garcia
Hi fellas,

First, I want to congratulate the NREL team for the excellent program they have developed.

I would need your help because I have some problems modeling my hybrid system.

I need to model a system that currently has PV+Wind, and I want to add batteries to it. To do this, I have combined the wind and solar productions into a 8760-value production matrix and introduced it into the system in the Generic-battery Merchant system.

Let me give you some context:
- Grid interconnection limit = 6 MW
- Nominal power PV+Wind = 10 MW
- Desired bank power = 2 MW
- Desired bank capacity = 2 hours
- I have input a matrix of random energy selling prices (25 years)
- The system cannot charge from the grid, only from the PV+Wind system

When I analyze the results, I realize that during moments of high prices, if the production from PV+Wind is, for example, 5764.66 kW, I only need the battery to provide me with 235.34 kW. However, it provides 2103.36 kW continuously. I don't understand why it keeps discharging 2103.36 kW repeatedly.

Attached, you will find the SAM model. I would appreciate it if you could assist me with this.

Thank you very much!

   

File Attachment:

File Name: PV+WIND+BESS.sam
File Size:3,536 KB
Attachments:

Please Log in or Create an account to join the conversation.

  • pgilman
More
15 Sep 2023 20:58 #12504 by pgilman
Replied by pgilman on topic Issue with the DOD Results
Hi Antonio,

SAM's battery dispatch algorithm does not consider the grid limit, which is why it allows the battery to discharge at a higher power than required.

github.com/NREL/SAM/issues/181

Best regards,
Paul.