DC vs AC Capacity Factors
- abonakda
- Topic Author
Less
More
29 Oct 2022 16:41 #11614
by abonakda
DC vs AC Capacity Factors was created by abonakda
Hello SAM,
From what I read, capacity factor calculations always use the actual AC kWh electricity generated in one year in their numerator. This AC electricity must contain the effect of the overall derate factor. The denominator, however, could be expressed in DC (after PV panels) or AC power (after inverter) multiplied by 8760 hours. Question: Does this mean that AC power should include the contribution of inverter efficiency only and not the entire derate factor?
Therefore, is the following, correct?
AC CF = 175,200 kWh-ac / (95 kW-ac x 8760 h) = 0.21 or 21%
And would this be incorrect:
AC CF = 175,200 kWh-ac / (80 kWh-ac x 8760 h) = 0.25 or 25%
Many thanks!
Best,
Arman
From what I read, capacity factor calculations always use the actual AC kWh electricity generated in one year in their numerator. This AC electricity must contain the effect of the overall derate factor. The denominator, however, could be expressed in DC (after PV panels) or AC power (after inverter) multiplied by 8760 hours. Question: Does this mean that AC power should include the contribution of inverter efficiency only and not the entire derate factor?
Therefore, is the following, correct?
- Solar panel rated DC power = 100 kW-dc
- inverter efficiency = 95%
- Inverter output AC power = 95 kW-ac
- derate factor = 80%
- Power after overall derating = 80 kW-ac
- AC kWh generated in one year = 175,200 kWh-ac
AC CF = 175,200 kWh-ac / (95 kW-ac x 8760 h) = 0.21 or 21%
And would this be incorrect:
AC CF = 175,200 kWh-ac / (80 kWh-ac x 8760 h) = 0.25 or 25%
Many thanks!
Best,
Arman
Please Log in or Create an account to join the conversation.
- pgilman
Less
More
- Posts: 5423
31 Oct 2022 11:43 - 31 Oct 2022 11:43 #11618
by pgilman
Replied by pgilman on topic DC vs AC Capacity Factors
Hi Arman,
I am not sure there is a "correct" way to calculate the capacity factor. Any use of the capacity factor should be accompanied by a description of how it was calculated.
In SAM, the capacity factor is based on the nameplate capacity of the array (rated DC power at Standard Test Conditions) or inverter (maximum AC power output). It does not apply any derating factor to the capacity term in the denominator.
Best regards,
Paul.
I am not sure there is a "correct" way to calculate the capacity factor. Any use of the capacity factor should be accompanied by a description of how it was calculated.
In SAM, the capacity factor is based on the nameplate capacity of the array (rated DC power at Standard Test Conditions) or inverter (maximum AC power output). It does not apply any derating factor to the capacity term in the denominator.
Best regards,
Paul.
Last edit: 31 Oct 2022 11:43 by pgilman.