Hi Craig,
The array and inverter in your file seem to be mismatched. The diagram on the Losses tab of the Results page shows a large "Inverter MPPT clipping" loss, which suggests there may be a problem with the array design. On the System Design page, under "Subarray 1" and "Subarray 2" you will see that the String Vmp (string voltage at maximum power rating) for Subarrays 1 and 2 is 241.8 V and 483.6 V respectively. The inverter minimum MPPT voltage is 500 VDC, which means that it is likely the subarray operating voltages will never be high enough for the inverter to work. You can investigate that in the results by looking at the "Subarray [1/2] Operating DC voltage" and "Subarray [1/2] DC power gross" variables: It turns out that the operating voltage for Subarray 1 never reaches 500 V, so that subarray does not contribute to charging the battery. Subarray 2 does manage to reach the minimum MPPT voltage, but it can only charge the battery up to a maximum of about 47% state of charge.
One way to fix the problem is to adjust the number of modules per string in each subarray. I tried 13 modules per string for both Subarras 1 and 2, and set the number of strings in parallel for Subarray 1 to 1 and for Subarray 2 to 2. This results in an array size of 16 DC kW and avoids the clipping loss. With this array configuration, the battery results for the smaller battery look more reasonable to me.
Best regards,
Paul.