        How can I force the software to have a battery bank charge only from the system clipped power and have it discharge to the grid within a (6pm-10pm) time window?
I have tried using the automated dispatch: Input forecast but then the battery will discharge whenever by looking at the PPA price, electricity rate, costs of cycle, and inverter clipping. If I select Manual dispatch then I cannot control from where I would like to have my battery bank charged from.
Appreciate your help.
Pedro Sanches
    I have tried using the automated dispatch: Input forecast but then the battery will discharge whenever by looking at the PPA price, electricity rate, costs of cycle, and inverter clipping. If I select Manual dispatch then I cannot control from where I would like to have my battery bank charged from.
Appreciate your help.
Pedro Sanches
Please Log in or Create an account to join the conversation.
- Paul Gilman
 
        Less
        More
        
            
    
        - Posts: 5666
 
            
        
                08 Oct 2019 16:55                #7695
        by Paul Gilman
    
    
            
            
            
            
            
                                
    
                                                
    
        Replied by Paul Gilman on topic Dispatch Controller            
    
        Hi Pedro,
It is not possible to combine the automated dispatch and manual dispatch controller.
You could use the PPA price to control the timing of discharges by using a higher PPA price during times when you want to discharge and a lower price for other times.
Best regards,
Paul.
    It is not possible to combine the automated dispatch and manual dispatch controller.
You could use the PPA price to control the timing of discharges by using a higher PPA price during times when you want to discharge and a lower price for other times.
Best regards,
Paul.