SAM 2018.11.11 - Storage model bug?
- Gabriel Susca-Lopata
- Topic Author
Less
More
24 Sep 2019 15:36 #7674
by Gabriel Susca-Lopata
SAM 2018.11.11 - Storage model bug? was created by Gabriel Susca-Lopata
I am currently modeling a solar and AC-coupled storage system in SAM 2018.11.11. When I use the battery-inverter conversion efficiency of 98% proposed for my project, the simulation shows more total AC energy generated vs simulating with only the solar component; and in the summary graphs shows a "negative" 4% "AC connected battery loss". I noticed that to get a net positive "AC connected battery loss", I have to enter battery-inverter conversion efficiencies around ~80%. Could there be a bug in the storage model with the current version of SAM that I'm using?
Please Log in or Create an account to join the conversation.
- Paul Gilman
Less
More
- Posts: 5532
25 Sep 2019 12:03 #7679
by Paul Gilman
Replied by Paul Gilman on topic SAM 2018.11.11 - Storage model bug?
Hi Gabriel,
Did you change any other battery model parameters from their default values? The total AC output of a PV system should be more than the output of the same system connected to a battery because of electrical losses from the battery.
Would you mind sharing your .sam file so I can investigate?
Best regards,
Paul.
Did you change any other battery model parameters from their default values? The total AC output of a PV system should be more than the output of the same system connected to a battery because of electrical losses from the battery.
Would you mind sharing your .sam file so I can investigate?
Best regards,
Paul.
Please Log in or Create an account to join the conversation.
- Rob Frohne
Less
More
- Posts: 30
29 Jan 2020 00:00 #7916
by Rob Frohne
Replied by Rob Frohne on topic SAM 2018.11.11 - Storage model bug?
Hi Paul,
Was this resolved?
Thanks,
Rob
Was this resolved?
Thanks,
Rob