Cycle electrical power output (gross) | (MWe) greater than design gross output
- slrpp
- Topic Author
Less
More
03 Sep 2019 09:37 #7641
by slrpp
Cycle electrical power output (gross) | (MWe) greater than design gross output was created by slrpp
Hello, after simulating a 50 Mwh CSP trough plant, with no storage, I am getting a "cycle electrical power output (gross) greater than the parameter Design gross output, even when the Max turbine over deseign operation is set at 1.
I have tried several pairs of data: 50 Mw and 1.04, 52.4 and 1 and so more, getting values like 57 or even 62 Mw for gross outputs. I was able to limit the gross power to 52,4 by setting the design gross outputthefinally to 47,7 and the Max turbine over deseign operation to 1.
Thanks
I have tried several pairs of data: 50 Mw and 1.04, 52.4 and 1 and so more, getting values like 57 or even 62 Mw for gross outputs. I was able to limit the gross power to 52,4 by setting the design gross outputthefinally to 47,7 and the Max turbine over deseign operation to 1.
Thanks
Please Log in or Create an account to join the conversation.
- pgilman
Less
More
- Posts: 5423
03 Sep 2019 15:23 - 03 Sep 2019 15:24 #7647
by pgilman
Replied by pgilman on topic Cycle electrical power output (gross) | (MWe) greater than design gross output
Dear Raul,
The system should operate at the design point (50 MW gross in your example) under design conditions for incident irradiance, loop inlet and outlet temperature, cycle HTF mass flow rate, etc. that you specify as inputs.
In the simulation results, the exact design conditions are likely to be rare given the ambient conditions from the weather file. If you are trying to design a system that does not exceed a particular power output level, you should adjust the design parameters so that the system operates as you expect.
Best regards,
Paul.
The system should operate at the design point (50 MW gross in your example) under design conditions for incident irradiance, loop inlet and outlet temperature, cycle HTF mass flow rate, etc. that you specify as inputs.
In the simulation results, the exact design conditions are likely to be rare given the ambient conditions from the weather file. If you are trying to design a system that does not exceed a particular power output level, you should adjust the design parameters so that the system operates as you expect.
Best regards,
Paul.
Last edit: 03 Sep 2019 15:24 by pgilman.
Please Log in or Create an account to join the conversation.
- slrpp
- Topic Author
Less
More
- Posts: 2
04 Sep 2019 05:42 #7653
by slrpp
Replied by slrpp on topic Cycle electrical power output (gross) | (MWe) greater than design gross output
Thanks for the reply. I was running the Physical model. Once I changed to the empirical, the max output power was capped at what I asked.