- Posts: 11
Supercritical CO2 for Molten Salt Power Tower plants.
- jqcano
- Topic Author
Less
More
15 May 2019 19:46 #6796
by jqcano
Supercritical CO2 for Molten Salt Power Tower plants. was created by jqcano
Dear Paul,
I'm trying to simulate Gemasolar plant (Sevilla, Spain) with different power cycles. Now I'm trying the recompression sCO2 cycle, but I found this error when calculating the design point:
exec fail(sco2_csp_system): The compressor inlet temperature input was 87 [C]. This value was reset internally to the max allowable inlet temperature: 70 [C]
The turbine inlet temperature input was 35 [C]. This value was reset internally to the min allowable inlet temperature: 300 [C]
To solve the cycle within the allowable recuperator conductance, the design cycle thermal efficiency, 0.445, must be at least less than the Carnot efficiency: 0.401291
I suppose that I'm not misunderstanding some inputs:
Air cooler approach temperature refers to "compressor inlet temperature"?
PHX approach temperature refers to "turbine inlet temperature"?
Furthermore, any advise about any other cycles that I could simulate in SAM por MSPT plants would be welcomed!
Thanks for your help!
Javier.
I'm trying to simulate Gemasolar plant (Sevilla, Spain) with different power cycles. Now I'm trying the recompression sCO2 cycle, but I found this error when calculating the design point:
exec fail(sco2_csp_system): The compressor inlet temperature input was 87 [C]. This value was reset internally to the max allowable inlet temperature: 70 [C]
The turbine inlet temperature input was 35 [C]. This value was reset internally to the min allowable inlet temperature: 300 [C]
To solve the cycle within the allowable recuperator conductance, the design cycle thermal efficiency, 0.445, must be at least less than the Carnot efficiency: 0.401291
I suppose that I'm not misunderstanding some inputs:
Air cooler approach temperature refers to "compressor inlet temperature"?
PHX approach temperature refers to "turbine inlet temperature"?
Furthermore, any advise about any other cycles that I could simulate in SAM por MSPT plants would be welcomed!
Thanks for your help!
Javier.
Please Log in or Create an account to join the conversation.
- pgilman
Less
More
- Posts: 5423
06 Jun 2019 14:40 #7445
by pgilman
Replied by pgilman on topic Supercritical CO2 for Molten Salt Power Tower plants.
Dear Javier,
Those input variables are defined in the SAM help system (CSP Power Tower, Molten Salt Tower, Power Cycle, Supercritical Carbon Dioxide Power Cycle).
Best regards,
Paul.
Those input variables are defined in the SAM help system (CSP Power Tower, Molten Salt Tower, Power Cycle, Supercritical Carbon Dioxide Power Cycle).
Best regards,
Paul.