I’m having difficulty getting my battery to dispatch for a grid tied, stand-alone PV array with DC coupled energy storage.

System sizes are as follows:
PV: 4.66 MWdc, 3.63 MWac
ESS: 2 MWdc, 4 MWhr capacity

It’s a standalone system so there is no load. The desire is to produce at nameplate (3.63 MWac) for as much time as possible with kWh’s being stored in the battery that would ordinarily be clipped, then allow the battery to discharge as daylight fades to maintain 3.63 MWac of output.

Please Log in or Create an account to join the conversation.

  • pgilman
More
25 Sep 2018 11:27 #6445 by pgilman
Replied by pgilman on topic Battery not discharging
Hello,

In SAM 2017.9.5, power "clipped" by the inverter when the array output power exceeds the inverters rated input power does not charge the battery. In the next version of SAM, which we plan to release later this fall, clipped power will be available to charge the battery.

Best regards,
Paul.