Hello,
SAM's solar field freeze protection method assumes that the HTF flow through the field at night is recirculating: The HTF flows from the field outlet directly to the field inlet. SAM calculates the energy required at the inlet to maintain the HTF temperature at or above the freeze protection temperature value that you specify on the Solar Field page, and reports the energy value as the field freeze protection energy in the hourly results:
"Freeze protection energy" - Energy required to keep field HTF above the freeze point temperature
SAM also reports these two related values:
"Tank freeze protection energy" - Energy required to keep tank above the freeze point temperature
"Auxiliary heater fuel consumption" - Fuel (energy) used by fossil backup
In SAM, heating for freeze protection is assumed to be from electricity. The auxiliary heater fuel consumption and parasitic load are associated with the fossil fill backup system, which provides heat to the power block to supplement solar energy.
The time convention of the simulation depends on the time convention in the weather file. For the standard weather files (TMY2, TMY3, EPW), the first hour is the hour ending at 1 am on Monday, January 1.
Thanks for the Beta feedback suggestion. I will recommend that the two "HX approach temp" inputs on the Thermal Storage page be disabled when the heat exchange derate factor is 1.
Best regards,
Paul.