Trough system power estimates
- Jessica
Less
More
23 Apr 2021 19:02 #9514
by Jessica
Replied by Jessica on topic Trough system power estimates
Struggling to attach...
First question is:
I am using the SAM 2020.11.29 version, startup is still an issue.
At startup, the efficiency is given to be really low. If I use however values of efficiency from the next timestep I seem to get closer values. In your example:
If I use the first row, startup:
(218.4 - 62.36) x 0.199=30.97 this is less than the software generated gross output of 61.85.
However if I use 0.397 for efficiency (from next row)
(218.4 - 62.36) x 0.397=61.85 I obtain a very similar value.
do you know why this is the case? why are we getting strange values for efficiency while the gross output is computed at a higher efficiency assumption?
Second question is:
Can I confirm that the software does not consider any boiler back-up in the energy computations (I have seen some grid interconnections but not fossil fuel/boiler) ? is that physically possible?
Regards
First question is:
I am using the SAM 2020.11.29 version, startup is still an issue.
At startup, the efficiency is given to be really low. If I use however values of efficiency from the next timestep I seem to get closer values. In your example:
If I use the first row, startup:
(218.4 - 62.36) x 0.199=30.97 this is less than the software generated gross output of 61.85.
However if I use 0.397 for efficiency (from next row)
(218.4 - 62.36) x 0.397=61.85 I obtain a very similar value.
do you know why this is the case? why are we getting strange values for efficiency while the gross output is computed at a higher efficiency assumption?
Second question is:
Can I confirm that the software does not consider any boiler back-up in the energy computations (I have seen some grid interconnections but not fossil fuel/boiler) ? is that physically possible?
Regards
Please Log in or Create an account to join the conversation.
- pgilman
Less
More
- Posts: 5423
26 Apr 2021 16:27 #9532
by pgilman
Replied by pgilman on topic Trough system power estimates
Hi Jessica,
Please see the explanation here for an explanation of the efficiency during startup hours: github.com/NREL/SAM/issues/598 . We will fix the reported efficiency values in the next update to SAM.
The physical trough and power tower models do not have a backup fossil boiler.
Best regards,
Paul.
Please see the explanation here for an explanation of the efficiency during startup hours: github.com/NREL/SAM/issues/598 . We will fix the reported efficiency values in the next update to SAM.
The physical trough and power tower models do not have a backup fossil boiler.
Best regards,
Paul.